gokmen
Electrical
- Apr 8, 2009
- 6
Hello Friends, I have just joined this helpful site. I am an electronic engineer who is working as Operation and Maintenance Chief at a hospital. There are 2ea Alternators (SDMO-400V/50Hz/1000kVA) that are each driven by Diesel Engines (Cummins KTA50G1, 1500rpm/50Hz) as Emergency Power source for the building. The building's power demand is about 700kW. If any commercial power outage is detected both of the generators comes up and the generator-G1 connects to emergency busbar and first load group swithing to emergency side in 3 seconds. During this time generator-G2 decreases its speed and tries to synchronize to the emergency busbar. After the synchronization (about 30 seconds) period G2's C/B closes and coupling to emergency busbar is achieving. After this point G2 takes about 50% of the load on the busbar and other load groups connecting to emergency busbar sequentially. This is the scenario. Governor Setting is 1500 rpm with 1% droop for G1 and 1540 rpm with %3 droop. There are RG491 modules in each generator's control panels.
And the trouble I have on the Generator Sets is:
While G2 decreasing speed and trying to synchronize to G1, G1's speed begins to increase and after that G2 tries to increase the speed and catch the G1. Is that normal? What I think is G1 should remain at the adjusted speed at least untill G2 connects parallel and load sharing takes place.
Thank you very much for any help.
And the trouble I have on the Generator Sets is:
While G2 decreasing speed and trying to synchronize to G1, G1's speed begins to increase and after that G2 tries to increase the speed and catch the G1. Is that normal? What I think is G1 should remain at the adjusted speed at least untill G2 connects parallel and load sharing takes place.
Thank you very much for any help.