Borderline. This will not be suitable if there are any other loads on the generator. The Voltage and frequency drops when starting will be too much for most loads.
If this is a dedicated generator-pump application, it may be possible to start the motor. You may have to make provision such as a UPS to supply the control panel so that your controls will be able to ride throegh the starting voltage dip.
I would NEVER advise a customer to purchase that gen-set to start that motor. However, I understand the pressures you may be under to make existing equipment function.
When that pump is started on that set, the load will cause both the voltage and the frequency to drop. Lights will dim annoyingly and relays and contactors may drop out. However, the speed and frequency drop will activate the UFRO (Under Frequency Roll Off) feature of the AVR (Automatic Voltage Regulator) and maintain close to the optimum Volts per Hertz ratio for the motor. Now the gen-set is acting in a similar manner to a VFD, and will accelerate the motor up to speed. As the motor comes up to speed, the load will reduce and the AVR will ramp up the voltage. This is actually easier on the motor than a DOL start on a firm grid, and much easier than a DOL start on a soft supply.
This is a standby rated set. If this were a prime power rated set, there would be a 10% margin of overload available. Great if you buy a prime set rated at 87 kW but in this case, this set would be rated at 80 kW for prime service.