Generator reactance tolerances
tefc
FR
I'm currently performing a short circuit study.
For this calculations, the generators direct-axis subtransient reactance is required. At this stage, I know the expected value of this reactance (unsaturated & saturated value), however I've also to apply tolerance according to ANSI C50.10.
Could someone provide me with tolerance defined in ANSI C50.10. Thanks in advance.
Suggestion: Please, would you be more specific about those tolerances defined in ANSI C50.10. This is not exactly a tolerance citing standard.
IEC is +/-15%. It is usually practice to take the -15% which gives the worst case reactance after factory test and gives the maximum possible current.
I cannot imagine ANSI is much different.
jbartos, kevd, thanks for your replies.
jbartos, my concern is I don't have the American Standards defining the applicable tolerance on the expected value of the direct-axis subtransient reactance (I assumed it was ANSI C50.10, but maybe I'm wrong).
As suggested buy kevd, I've used the IEC tolerance (-15%), but I've to perform my calculations according to American standards. So this is still an issue.
It should not be an issue if you state in your calculations all assumptions made.
Suggestion:
1. IEEE Std 115 test generator for short circuit parameters. However, the Xd" accuracy is often specified in the generator spec, e.g. plus minus 10%
2. Visit
and check with generator manufacturers
3. Military standards requires for the Xd" measurement that the generator speed tolerance is plus minus 1% and measuring accuracy is plus minus 0.5%.
See
MIL-STD-705C
24 April 1989
SUPERSEDING
MIL-STD-705B
26 June 1972
MILITARY STANDARD
GENERATOR SETS, ENGINE DRIVEN
METHODS OF TESTS AND INSTRUCTIONS