Power would flow North to South and every generator would be turning slightly slower than the one above it. Not enough to motor or skip poles, but just enough to be lagging physically.
Hi Gunnar, Let's hit the pub. Like you, I'm off drink but I feel a desperate need for a tall Pepsi, Straight Up, in a Dirty Glass. I'm guessing that you could use something similar. First round's on me.
Historically a group of parallel generators would be operated in droop except for one swing set that corrected frequency errors for the system.
The base load sets used droop to control loading.
At a set point of 60 Hz, a generator would not be supplying any real energy to the system.
It may be overexcited to supply reactive power but that is a topic for another day.
To load a generator up, the set point would be advanced.
With 5% droop, if the frequency is set to 101% of 60 Hz, or 60.6 Hz the set will pick up 20% load.
The set is running at a nominal 60 Hz but the governor is set at 60.6 Hz.
At a governor setting of 102.5% of 60 Hz or 61.5 Hz the set will be running at a nominal 60 Hz, and 50% loaded.
For those with an instrumentation background think of 5% proportional band plus 5% offset. That's droop.
In the old plants there was a control marked UP-----Down or something similar. This was the governor control. When a generator was running but not paralleled this control controlled the speed/frequency. The operator could increase the speed/frequency with this control.
Once the generator was in parallel with the system, the control no longer controlled the speed/frequency. Those were locked in to the grid frequency.
Now the same control controlled the load on the set rather than the speed. What changed? Is there some fancy switch over circuit that transfers control from speed control to load control?
No. The control still controls the governor. Now as the governor is advanced, when the generator can not speed up, the droop or proportional action of the governor adds more fuel trying to speed up, it can't speed up and so takes on more load instead.
Now what happens when a large load hits the system? All the generators respond together and the system frequency drops a little due to the droop action of all the governors.
The controls on the swing set see that the frequency is no longer exactly 60 Hz and starts to pick up load to correct the frequency.
As the swing set is picking up the load, the frequency on the entire system is increasing until it stabilizes at 60 Hz or until there is another load change.
Another advantage to running in droop as well as the ease of loading sets is that in the event of loss of load for one or more generators, the droop control will limit the speed setting to 105%.
All the generators in a system run in synchronism at the same frequency.
Due to load changes, the frequency is continually varying a small amount and the swing set is continually correcting the errors in frequency.
We have seen some frequency graphs that show varying frequency on systems. It would be interesting to see the graph of the loading on a base set. The frequency chart and the load chart should mirror each other fairly well. (Yes, the scale will have to be adjusted to allow for a number of factors.)
That's the way it used to be.
I've been away from generation for a while now. Has there been any changes or is the same basic system used today?