Issue number 2. Radiator maintenance.
There is a fill line on the radiator. Do not overfill the radiator.
I had a lot of customers who had a yard boy who serviced the standby generator.
Every Monday they would fill the radiator to the very top.
The next Saturday or Sunday, during the weekly outage, the coolant would expand and push some coolant out of the overflow.
After a year or so, the original coolant with the corrosion inhibiting properties would have all been replaced by water.
Not good.
One customer had a more educated worker. He topped up every week with anti-freeze. (In the tropics)
After a year or so, the set was cooled by almost 100% anti-freeze.
The floor in the generator room was green and very slippery.
A year of losing anti-freeze on the floor will do that. (No smoking please.)
Issue number 3. Oil changes.
When you change the oil, changing the oil filter is even more important than new oil.
Look at the exhaust system every few years. Exhaust piping on standby sets tends to corrode.
Fairly short, infrequent running and lots of condensation left behind after a short run will do that.
If the exhaust stack is vertical, try to put a bend on the end. That is more permanent and more dependable than a flap valve.
You did check the flap valve didn't you?
--------------------