Background:
We are purchasing a 200KW genset for standby service duing a natural disaster at our plant. The genset is purely for logistic functions for making facility repairs before the utility can get back online. The bulk of the required loads are on one 480V substation, but there are required loads in two other 480V substations. These 480V substations are fed from our 13.8KV distribution system by 13.8KV-480V, delta-wye transformers that are solidly grounded at the X0 busing on the 480V side. The plant takes power from the utility at 13.8KV from the utility's 69KV delta-wye transformers that are low resistance grounded at the neutral.
Question:
Assuming the utility is isolated by opening the incoming circuit breakers, can the genset backfeed the 13.8KV plant distribution system? If so, what about grounding the 13.8KV side? Is a zig-zag transformer required? The NEC applies in this situation.
We are purchasing a 200KW genset for standby service duing a natural disaster at our plant. The genset is purely for logistic functions for making facility repairs before the utility can get back online. The bulk of the required loads are on one 480V substation, but there are required loads in two other 480V substations. These 480V substations are fed from our 13.8KV distribution system by 13.8KV-480V, delta-wye transformers that are solidly grounded at the X0 busing on the 480V side. The plant takes power from the utility at 13.8KV from the utility's 69KV delta-wye transformers that are low resistance grounded at the neutral.
Question:
Assuming the utility is isolated by opening the incoming circuit breakers, can the genset backfeed the 13.8KV plant distribution system? If so, what about grounding the 13.8KV side? Is a zig-zag transformer required? The NEC applies in this situation.