For Iris coupling capacitor equipment, an appropriate alarm level for a 13.2kv air-cooled machine is roughly 400 millivolts.
It will vary by:
voltage level
cooling type
sensor type (coupling cap or slot coupler)
equipment vendor (Iris, Adwell, Cutler Hammer)
Iris publishes rough limits based on statistical analysis (worst 10%) for each class of machines (voltage level, cooling type, sensor type).
Of course trending with historical results and comparison with similar machines are the most effective techniques. In my database I compensate for the effects of temperature and humidity by determining temperature coefficient and relative humdity coefficient of partial discharge through linear regression analysis of pd results for each machine. Then I can trend the corrected results with the variability introduced by those variables removed.
=====================================