kh2,
Can I comment on your list?
1) A dedicated generator / GSU block is equally 'logical', perhaps more so because the GSU is a dedicated purpose transformer and isn't involved in other functions like supplying house power.
2) The differential zones can still be designed to provide a highly discrimatory scheme with well-defined overlaps between zones.
3) Agree, although whether the reduction in fault energy would be enough to save the transformer is a different question.
4) Depends on the station auxiliary design. Most generators require maintenance, as do GSU transformers. With a GSU providing house power the GSU can't be maintained without shutting down the site. This is especially a problem on smaller single machine, single-shaft CCGT stations where there is only one GSU and there's no alternate supply from the transmission system or utility. If you have multiple GSUs, each with an auxiliary transformer, then it's an arguable point.
1) If you have a separate station auxiliary transformer then you save a GCB, but have to install an extra breaker in the transmission substation.
2) Agree.
3) Hahahahahaha! You just go trouble-shooting in the dark instead, because there's no house power. Seriously, troubleshooting is just as bad with either system.
4) There'll be less maintenance because you won't be able to release it for maintenance. Then one day it will fail through lack of maintenance and you'll be waiting about two years (last time I looked) for a new GSU transformer.
----------------------------------
If we learn from our mistakes I'm getting a great education!