Dear JLuc.
Could you please answer on one, not so correct Q.
Who are you, end-user, main contractor, subcontractor or designer in this project?
I put attention on your several Q's on the last time, as, OLTC use or not, CB's use or not, etc.
Please don't take this , as some sort of negative Q's, I'm only try understand, you are technical guy or project manager or salesman.
If you only technical, my answer for you:
Is not "good" design for the new industrial substation
1. Trafo paralleled w/o separated CB's
2. Plant with full load about 40MW on the two xfr's w/o OLTC. I've never see industrial plant w/o variable load.
3. More from this : you have two parallel xfr's, that mean you also must parallel operation of OLTC control.
4. Series connection of several diff protection, today???, additional cores or CT's is not issue
If you project manager with money problems, becouse your bosses wined this project with dumping price, will try make min of min, but not base it on some right technical solution.
If you end-user, EE of this plant, sorry, I'm don't understand you. You need work with this in future.
I'm also project manager and usually work as subcontractor of big companies, have same problems, but cost is cost,
technical responsible is responsible.
Regards.
Slava