Well of course it is possible.
Gas pressure builds up inside the compressor staging of the CT (combustion turbine compressor) to 6 to 11 atmospheres pressure - depending on the size and age of your compressor's design. older units could not get to the pressures newer ones do, smaller units won't get as high a pressure as larger units with larger (more) compressor blades.
There are drains (normally shut of course) off of the bottom of the compressor casing at several points. All of these drain points will be pressurized under operation, if there was water (fuel ?) in the casing that water will come out when the drain valve is opened after startup. Once bled dry, there shouldn't be more water coming out unless you are running inlet (cooling) water spray that is not fully evaporating .
There will likely be drain valves under the casing so the power turbine can be drained as well. Possible sources of fluids are un-burned fuel, water spray if you're not running, rain water into an open turbine casing under repair, possibly water coming back down the exhaust stack if you were not running the past day or so. Could be a lube oil leak through a bad bearing seal that sprays into the drained area.
Once the