We've been having occasional gas seal failures on a multistage centrifugal wet gas compressor in our refinery. The failure was determined to be wet gas condensation (since the eht) on the flush line from the compressor discharge does not work reliabiliy and we are up north in Canada. The compressor start up sequence calls for nitrogen based start-up to the primary, second and teritery seals and once the compressor achieves stable operation. The seal flush is then changed to compressor discharge. But because of the condensation issue we are planning to run the compressor on nitrogen the entire time (with certain modification to the start/stop permissive) we have regulated nitrogen header pressure and in case we would run into issues with this header pressure we are planning on using the emergency back-up nitrogen skid bottles to trip the compressor in a controlled manner.
I realize this is a deviation from the SOP for compressors and the associated gas seals. However, would like your thoughts on what modifications (if any) would be required on the compressor to achieve the above senerio. I trust it should be as simple as plugging or blinding the flush line from the compressor discharge to the seal. This should take care of the wet gas from not flowing to the gas seal anymore and using external nitrogen from the main supply header. Also, are there other issues using nitrogen in a such a fashion for compressor reliability.