Gas Cabinet

Status
Not open for further replies.

jimnogood

Mechanical
May 1, 2009
21
Forum,

What are requirements for having a sprinkler inside a gas storage cabinet, such as the type found in a laboratory? The room itself is fully sprinklered. I could not find anything specific in NFPA 45, 30 or 55 that requires a sprinkler.

Thanks.
 
Replies continue below

Recommended for you

Have not seen them in there and IFC does not appear to require them

Are we talking single cylinder cabinets???
 
Sometimes the gas storage cabinets, especially if it is a particularly hazardous or toxic gas are pre engineered with exhaust and fire suppression already installed with connections for building supply.

All you have to do is give it a pipe to connect to.
 
Where's the gas cabinet and what's it storing because it makes a big difference. In the IFC, the only time gas cabinets require automatic sprinkler protection is in Group H occupancies and only when it is storing flammable or pyrophoric gases.

Now if you're dealing with silane in concentrations > 1.37% V/Vair, CGA P-13 always prescribes sprinkler protection in any gas cabinet, including cabinets for lecture bottles.
 
The cabinets on my project dealt with had arsine, phosphine - of which I was told arsine will kill you in levels in ppb.
 
This is in a B occupancy. I am awaiting an answer on what is going to be stored in the cabinet.
 