Jeffduk
Electrical
- May 11, 2004
- 3
Hi
new to this forum, but it looks very helpful.
my question is this: I am trying to select an REC Cut-out fuse (BS88) that will not rupture whilst powering up a 125kVA transformer. The inrush rating given by the manufacturer is 5 times full load current. i understand that whilst looking at a fuse characteristic curve i can see whether the fuse is clear of this inrush current.
The problem i have is that i am unsure on how to calculate the I2t (energy let through) created by the transformer on inrush. the equations i have found are 5xfull load = 1600A squared = 2.56MA x 0.1 secs = 256kA.
this high value is posing a problem, which is why i seek clarification on how to calculate this value as i have a feeling i am wrong. I am sure there must be another method as the above equation is normally used for a short circuit fault, but with current inrush the current starts high and then normallises after a few cycles.
thanks for any help you can give.
new to this forum, but it looks very helpful.
my question is this: I am trying to select an REC Cut-out fuse (BS88) that will not rupture whilst powering up a 125kVA transformer. The inrush rating given by the manufacturer is 5 times full load current. i understand that whilst looking at a fuse characteristic curve i can see whether the fuse is clear of this inrush current.
The problem i have is that i am unsure on how to calculate the I2t (energy let through) created by the transformer on inrush. the equations i have found are 5xfull load = 1600A squared = 2.56MA x 0.1 secs = 256kA.
this high value is posing a problem, which is why i seek clarification on how to calculate this value as i have a feeling i am wrong. I am sure there must be another method as the above equation is normally used for a short circuit fault, but with current inrush the current starts high and then normallises after a few cycles.
thanks for any help you can give.