Below Is an impartial attempt to summarize the pros and cons of use of power fuses vs. relays for distribution transformer protection based on this post recommendations, accepted industry practice and some degree by personal experience;
PRO
a) Fuses used in the power industry are reliable with infrequent failure rate.
b) Fuses are self powered. No need of DC, CTs, or low voltage wiring; all possible failure points.
c) Fuses are great to protect VT’s.
d) Fuses are simple thermal devices and very economical to purchase and maintain.
e) There is high probability that fuses has unlimited life if loaded under 60% of the rated current. The worst performance is estimated for 90% loading factor with frequent loading cycles.
f) If fault current is extremely high, a fuse can be faster than a breaker Fuses can clear faults within 0.5-2 cycles after inception. The fastest type are “current limiting fuse” (CLF) but careful selection is advised to clear the inrush current and avoid nuisance tripping.
.
g) For lower fault current a ‘fast grounding switch” is an alternative to improve the clearing time. However, this approach will increase cost and still create O&M and reliability challenges.
CONS
1. Potential for single phasing. Single phasing causes very high negative sequence voltage and current and low voltages (Line-to-Neutral & Line-to-Line).The resultant voltage may be worse than no voltage due to the overheating that it can cause to certain types of equipment, such as three phase motors.
2. Fuse link require replacement after fault This could increase outage and maintenance time. CLF fuse can be damaged by inrush current if not properly selected.
3. Poorer protection when compared with breaker + relays. a) Fuses are slow to operate at low & moderate current. i) Time for fuses to blow is much slower than proper breaker. ii) Fuses will not sense low level faults, such as near the neutral of the transformer, and hence trip only after the fault has evolved into a high current event. iii)This put the transformer at higher risk for being irreparable after an internal fault and at higher risk of failing in some catastrophic manner, such as a fire. iv) The low sensitivity of fuses means they are poor at backing up secondary overcurrent protection devices, especially for faults remote from the transformer secondary and especially for ground faults on delta/wye transformer banks. .
. b) Fuses cannot provide overload.
i) To allow short overloads, a transformer fuse is typically selected to carry per the NEC 150-300% of the transformer rated current. ii) Most fuses can carry over 125% of rated current for very long times. iii) and just begin to reliably trip for faults in the range of 150-200% of the fuse rating, and at this level generally take tens of seconds to trip. The effect is that a fuse might carry current in the range of 3 to 5 times transformer rated current for an extended period.
4. Fuses are susceptible to aging degradation i) Fuses are subjected to gradual damage from heavy through faults, leading to an eventual fast trip for a low magnitude fault. ii) Fuses are not as precise in operating characteristics. Characteristics change slightly with temperature, pre-fault and loading cycles. iii) Moisture is recognized of one of the multiple stressor that can lead to failure. However, the predominant failure mode (80%)is attributed to the fatigue of the fuse link over long operation time due to exposure to elevated temperature, voltage transients, or short duration over current condition.
5. Fuses have a much lower fault current rating This could limit the application for smaller units than circuit breakers.
6. Lack of event reporting & monitoring features. i) If a fuse blows, probably the transformer have to completely redo Doble/oil testing before re-energizing the transformer resulting in increasing outage time. quote: ii)Prior to getting rid of the 115 kV fuses, we had several fuses blow and no transformer failures.
c) Fuses can not sense current unbalance as relays does with small flow of current for relays differential protection. In the absence of a fault in the protected zone, this unbalance tends to be small and the flows into the zone are closely matched to the flows leaving. Accordingly, such relays can be more sensitive than phase overcurrent relays and need not be delayed to coordinate with other relays during external faults.
7) Transformer MVA Size & primary voltage kV Those parameters alone are not a definite guide for transformer protection and should consider reliability, maintainability and life cycle cost. i) Fuses are the predominant choice for transformers below 10 MVA and 15 kV class probably influence by general recommendation developed years ago. ii) Under 3MVA, breakers on the high side are seen only in special applications (e.g., some small generation sites may use a high side breaker). iii) The cost of protection and ancillaries equipments is marginal for large transformers. iv) Important units requires relay system to protect the asset and achieve high reliability and maintainability.