If you're going to wash your hands of the transformer as soon as it's powered up, sure put in fuses. But if you, or a future you, is going to replace that transformer at end of life and future-future you is going to replace that one, you'll find that a full protection package is far less expensive that doing it half-arsed with fuses. Never seen a decent event file from a fuse. Never seen a delta high-side fuse that clears a wye low-side SLG fault in anything close to a reasonable amount of time.
I've had a transformer with differential trip within cycles of a high-side turn-turn fault, way before any fuse would have done anything. I've had a fuse protected transformer spew oil all over the place (fortunately no ignition) because the fault was deep enough to not blow fuses faster than the line trips; a low enough magnitude fault that the line tripping took long enough that the reclosing reset between trips. Fuses are great for VTs, but not for real transformers.