EddyWirbelstrom
Electrical
- Feb 17, 2002
- 216
For arc-flash analysis the fuse ‘total clearing time’should be used.
IEC Fuses
In the IEC world, fuse manufacturers publish fuse time-current characteristics which plot the ‘pre-arcing time’ as a function of rms prospective current. IEC 60269-1 states that for times longer than 0.1 sec, the difference between ‘pre-arcing time’ and ‘operating time’ is negligible.
The ‘operating time’ is the total clearing time which is the sum of the ‘pre-arcing time’ plus the arcing time.
American Fuses
In Amercian fuse catalogs I have seen fuse time-current characteristics plotted as :
- ‘minimum melting time’,
- ‘minimum melting time’ and ‘total clearing time’.
as a function of rms prospective current.
Questions
IEC Fuses
• What +/- tolerance should be used for the ‘pre-arcing time’ ?
• What additional time should be added for times below 0.1 sec for the ‘operating time’ ?
American Fuses
• What +/- tolerance should be used for the ‘minimum melting time’ ?
• Where only the ‘minimum melting time’ is published, what time should be added for the ‘total clearing time’?
IEC Fuses
In the IEC world, fuse manufacturers publish fuse time-current characteristics which plot the ‘pre-arcing time’ as a function of rms prospective current. IEC 60269-1 states that for times longer than 0.1 sec, the difference between ‘pre-arcing time’ and ‘operating time’ is negligible.
The ‘operating time’ is the total clearing time which is the sum of the ‘pre-arcing time’ plus the arcing time.
American Fuses
In Amercian fuse catalogs I have seen fuse time-current characteristics plotted as :
- ‘minimum melting time’,
- ‘minimum melting time’ and ‘total clearing time’.
as a function of rms prospective current.
Questions
IEC Fuses
• What +/- tolerance should be used for the ‘pre-arcing time’ ?
• What additional time should be added for times below 0.1 sec for the ‘operating time’ ?
American Fuses
• What +/- tolerance should be used for the ‘minimum melting time’ ?
• Where only the ‘minimum melting time’ is published, what time should be added for the ‘total clearing time’?