Friction loss of grooved coupling joints 1

Status
Not open for further replies.

16121975

Mechanical
Joined
Nov 12, 2010
Messages
1
Location
NL
Hello Everyone,

I've a question about jounts. In particular about grooved joints. Is there something written in the NFPA13 about this.
And if so; what value is recommended for the friction loss.
But most important, is it somewhere enclosed in the NFPA 13.

Thank for your time.

Patrick
 
NFPA doesn't list this explicitly as a required pressure loss. Grooved pipes butt up against each other, and are therefore calculated as a single run of piping, with the pressure loss being calculated with the Hazen-Williams equation. The c factor is used to account for friction inside the pipe.

If it's a dry system, make sure the couplings have flush seal gaskets, and use the appropriate c factor to account for increased friction inside the pipe.
 