We have a situation where two gas engine generators, 800 kW, 600 VAC had been running in parallel when one of these units started exhibiting significant frequency swings to the point where operations have taken it off line.
Each of these have Woodward 721 digital governor controllers with load sharing compensation and reactive power compensation features, both incorporated into the design of controls for these generators.
A similar incident occured two years ago; it turned out that the vent line on the I/P converter on the main fuel valve was plugged,not allowing the I/P to regulate the flow of fuel as called upon by the governor. This problem was rectified and tubing re-run to minimize this occurence.
Other than the above as a possible culprit, do you know of any other possibility that could present this type of frequency swing (when in parallel with another unit). Any good troubleshooting ideas? Operations do not believe that this problem could be fuel-related, and have focussed their cross-hairs on the engine controls.
Thanks,
Phlipper
Thanks,
Phlipper