Hi Prot123,
A major Australian utility where I used to work applied earth leakage
protection quite extensively on double bus 11 kV metalclad switchgear.
Frame leakage was used because of the difficulty of applying high impedance
protection on a board where breakers could be racked to either of two buses.
The scheme works, but there are a number of traps:-
- Need to ensure good frame isolation from ground. A frame - earth insulation
of > 10 ohms was the set standard, and the schemes were installed with a built
in system for periodically measuring the frame isolation impedance.
- The need to work out what should be tripped. A selection scheme was used which
tripped any feeding transformers with starpoint earth current flowing.
- Frame currents associated with feeder faults. The scheme had a feature which
delayed FL tripping when significant earth current flowed in an outgoing feeder.
The scheme cannot be relied upon to detect phase faults not involving earth. Most
faults in metalclad boards involve earth, and the intention is to speed up clearance
for these. Three phase faults and pure phase-phase faults need to be cleared with
overcurrent.
If I were designing a new station, I would look closely at schemes like Low Z
differential and OAFD as alternatives. I wouldn't completely dismiss FL though -
especially for brownfield - it has its uses.
Thanks,
Alan