Folks,
When you calculate the uplift load on a footing, the code requires the use 0.6D + W. Assume this gives a net uplift of 30 kips.
When you calculate your resistance to uplift in terms of the footing weight and the weight of a truncated soil pyramid (based on a 30 degree angle), do you use a 0.6 factor on the uplift resistance and compare it to the above calculated uplift of 30 kips?
It seems like double dipping (very conservative) to use a 0.6 factor on the resistance side also. Thoughts?