DrDrreeeaaa
G'Day All
We are currently in a cost and benefit exercise regarding the specification of VSD cable.
Our project is a new manufacturing plant requiring the installation of ~120 VSDs (VVVF drives). Here is some key data for this discussion:
1) Drive sizes - 0.37kW to 90kW
2) Drives are AB Powerflex 525 and 753
3) Distance from drives to motors is around 100m
4) The drive cables will be installed on ladder probably touching other, non shielded control cables.
4) Drive cables are required to be steel wire armored (SWA)
The installing contractor has a significantly cheaper offer for the supply of VSD cable having only one of a braid screen or a foil screen, but not both.
What do you think the best option is, foil screen (laminate tape) or braided screen?
From my understanding the tape provides a lower transfer impedance for higher frequency noise, while the braid is more suited for lower frequency noise.
In addition, the benefits of SWA for shielding have been debated considerably and, in the past, I have not considered SWA to provide any shielding benefit. However, practically, it probably will provide some shielding for low frequencies - hence with respect to having to choose between foil or braid, perhaps the combination of SWA and the foil is the best option?
Any thoughts are much appreciated
Regards, Michael.
Regards, Michael.