Hmmm,
From what I have read so far, it appears as though there may issues on both side of the service line. CML D.I. can deteriorate over time, but more importantly, if the prpoerty owner has never flushed lines onsite, and the municipality has equally not exercised the hydrants, a buildup of material in the main can accumulate over time, particularly if the source was has a high turbidity and the treatment process does not always or cannot remove all particles. That may be one source of the material your mentioned.
Regarding the loop, maybe I missed something but if the existing 8" is connected to the 10" in a looped effect, the problem is now only being made worse.
Since the land use is retail and the 10" was sized to accomodate sprinklers, I assume that the 8" was sized for that purpose as well. Both lines are sourced by the 12" municipal main. I don't even have to run a hydraulic model to know that the water is going to flow in the path of least resistance, however since we are only referring to ADD or MDD flows, the velocities in those pipes are likely not going to change very much from what is is today....the square footage of the buildings are pretty much the same. The loop is not going to cause a flow through because the water demand is exclusive for the site itself, unless the municipal main runs through the site, at which case this discussion would be moot. Since the 10" and 8" are already sized for sprinklers, looping them may help only in the case of improving flow to the building. Since the fire flow is provided by the municipal line, I would wager a guess that the flow improvement in this case would be marginal - maybe 10 or 20 gal/min...maybe more, depending on the system.
The bottom line is that since improvements to the site will occur, flushing hydrants should be installed and a program be adopted for annual or semi-annual flushing of the lines should occur, hopefully in conjunction with the municipal program.
KRS Services