Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Flow rate for Plate Heat Exchanger

Status
Not open for further replies.

siiruy

Marine/Ocean
Joined
May 17, 2009
Messages
9
Location
MY
Assuming I have a pump which supplied water to PHE (cold-side) at 50m3/hr.

what happen if the supply of water is decrease since i'm want to tap that line for other services?
 
You outlet temperature will increase on both sides.

Best regards
Morten
 
Thanks Morten,

is there any way to overcome this problem without changing the pump?
I'm thinking to add more plate cooler as to increase the effeciency of heat tranfer rate.
any advise?

 
Increaseing the heat transfer area could mean that your hot side could remain unchanged - your cold side will however increase (even more). You will have to do a temperature cross check.

Best regards

Morten
 
Reducing flow or adding plates will reduce the pumped water side velocities and the heat transfer coefficient will fall off fast. Reducing flow will also reduce the bulk water flow reducing the overall duty capability of the Hx at any heat transfer coefficient.

You could, however check with your Hx vendor about two passing your cold water side (or both).

rmw
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top