The CBC (california) limits FMC to 6' lengths. however, this can be
modified/changed by the EE, by insuring that there is a grounding conductor within the flex.
The reasoning behind the short lengths is grounding (who would have thought).
The CEC, NEC, NFPA all have listed locations where you can not have Flex, not be confused with liquatite, such as, but not limited to, underwater, battery rooms etc.
steve
Inspector Steve
DSA, OSHPD, Inspector
So. California.