dik,
They go a lot higher than 30 storeys.
Zambo,
Single strand bonded tendons are not economical. The smallest economical tendon size is normally 4 strands. VSL tried a 2 strand system in USA several years ago but it was very expensive and uneconomical (and they went broke). In normal slabs, bonded PT requires spans of about 7 metres to justify the use of 4 strand tendons and maintain reasonable tendon spacings. However with your very heavy loadings you could use 4 strand tendons in your slab.
With a slab this thick and with such short spans, I would use a mat of straight tendons top and bottom rather than draped tendons. Draped tendons would have too much losses.
You could save on concrete and steel but which would be most economical would depend on the local costs for RC versus PT.
You would also have to be wary of horizontal restraint effects in the slab from the piles.