Although application of a N2 blanketing system is certainly recommended, I do not think that it is required by international regulations.
Reason why I think this, is that the international standards on Hazardous Area Classification (i.e. API RP 500, IEC 60079-10, IP15) classify the volume in a fixed roof storage tank above the flammable liquid level as Class I, division 1 (API) or zone 0 (IEC, IP). This classification means that a flammable mixture is expected to be normally present there.
With a N2 blanketing system you would expect a lower classification (e.g. zone 2), since a flammable mixture would only be present in case the blanketing system fails.