Has anyone seen this before .
We have a project where all the joists are going to be free hand sprayed with fire proofing 2" thick .
So instead of having 4" wide bar joists I now have 8" wide barjoists at the bottom . And with these heads being Extended coverage heads the 4Xs rule is really testing my patience .
(I need to be 32" to clear the obstruction) . I just can't get the heads spaced correctly . And these heads were specifically spec'd for this job by owner .
Thanks .