fire wall - existing pre-eng bldg

Status
Not open for further replies.

rittz

Structural
Dec 30, 2007
200
A Contractor friend of mine erected a pre-engineered steel building. The inspector informed him that it violated the limiting distance requirements on the side wall and wants a two hr rating on the side wall (160 ft long x 18 ft eave ht). The building is a typical pre-eng with rigid frames at 20 oc, w/ girts and 24 gage o/s sheeting. Has anyone had to do something like this after the fact.

There is a jog in the wall so that half of it requires only 1-hr rating
 
Replies continue below

Recommended for you

seems more like an architectural question unless you are asking us about designing some type of break away wall....?
 
What is the building occupancy and classification?
 
Check out UL fire ratings U425, U489, and V421.
Each of those has the potential of a 2-hour rating with an appropriate number of layers of drywall. Note that if you are needing a rating for an exterior fire source it may be necessary to get a layer of drywall between the girts and the exterior siding. (Obviously problematic on an existing structure).
 