More scary stuff: In reading through the pprune.org web site, someone posted a sumary of a similar 777 incident. In it, the AAIB (UKs version of the NTSB) made the following reccomendation:
"To implement differential current fault protection of main power contactors when designing future electrical systems"
Huh? Back in my days on the 767, 747, and 737 power systems, we had differential protection zones out to the primary load buss breakes and overlapping zones covering the GCB and BTBs. What happened? Did someone decide it was a good idea to eliminate it?
Arcing faults often do not reach overcurrent protection trip levels. As a result, faults can often persist for seconds, or minutes. Spraying molten metal all the while. Either differential or arc fault detaction schemes are the only reliable way to deal with such faults.