I have been given a table of fire flows at various hydrants by a city. A column provides a calculated flow rate for the given hydrant at 20 psi, the max fire flow if you will. I cant remember the equation used to determine this rate. I seem to remember it is a form of the energy equation. As with standard fire flow tests, I have static and flowing pressures at two hydrants. I dont want to solve it graphically. Does anyone have this worked out with the conversion factors to get it in standard units? thanks
 
Nothing better than answering your own question...

The equation is

Available water = Q mutliplied by square root(D2/D1)

where available water is flow rate in gpm
Q = flow rate of flowing hydrant in gpm
D2 = static pressure - assumed residual pressure of 20 psi
D1 = static pressure - actual residual pressure

leadfeet
 
Thanks, cvg. I had gotten used to using the .54 log graph method at my other job. I don't have any of that paper here, and I needed a quick, no-frills refresher.

If anyone else needs a summary, this is a page or two that cuts to the chase.

Remember: The Chinese ideogram for “crisis” is comprised of the characters for “danger” and “opportunity.”