Fault Current Distribution in a ZNyn1 (22kV/0.440kV) Transformer
Prot123
AU
Hi All,
I have a question about fault current behaviour in a ZNyn1 (22kV/0.440kV) transformer, which is being used as an earthing and auxiliary transformer.
For a line-to-ground (LG) fault on the LV (yn) side, my calculations show a very low fault current, which seems to align with standard guidelines and references (e.g., JP Transformer Handbook). However, I want to double-check a few things:
  • Is this expected, or am I missing something?
  • Does the zero-sequence balancing flux flow through the transformer tank on the yn side?
  • Would a buried delta winding help reduce zero-sequence impedance?
Additional details:
  • Zero sequence impedance is 20ohm/phase.
  • The Y side is solidly grounded.
Any input is highly appreciated. Thanks
If you are loading a ZNyn transformer with a single-phase load, a stabilising tertiary is a must. Please see the attached link for details. ( last sections)
How do Zig-Zag Earthing Transformers work? - Applications - Confluence (atlassian.net)