I have been struggling with external Fire and two-phase flow.
ASME Code says 21% vessel overpressure is allowed for external Fire.
The rules were written when only all vapor venting was generally considered.
So I have been using 10% overpressure for two phase flow based mainly on the assumption that ASME Code has not has not caught up with the modern world.
My client disagrees - the Code makes no distinction between all vapor venting and two phase flow.
Of course he is correct.
But as a PE, it is my "professional opinion" the 10% overpressure is a correct evaluation.
This is based mainly on the uncertainity in two phase flow engineering science.
Any comments would be appreciated.