For an exterior framed observation tower (park-like setting - open to the public) I am using 100 psf for the live load. I'm satisfied with the use of this.
For wind - this is in an outdoor environment and I've calculated the loads based on 90 mph Exposure C based on its location.
In combining D+L+W, ASCE 7-05 allows the use of the following load combination (ASD):
D + .75L + .75W
My observation of this is that they have statistically observed that the chance of a full live load and a full wind load occurring simultaneously is low - thus the 75% reductions are allowed.
This makes sense for a buildng where people WOULD occupy the building during a windstorm. However, this tower is outdoors and it seems that the chance of a full live load with full wind would be EVEN LOWER. Would you ever get even close to 100% LL with a heavy wind blowing? I don't think so. But it appears that I'm locked into the 75% reduction.
Does it make sense to lower that combination to this:
D + 0.5L + 0.75W
D + .75L + 0.5W
There's no code justification for it - just common sense?
For wind - this is in an outdoor environment and I've calculated the loads based on 90 mph Exposure C based on its location.
In combining D+L+W, ASCE 7-05 allows the use of the following load combination (ASD):
D + .75L + .75W
My observation of this is that they have statistically observed that the chance of a full live load and a full wind load occurring simultaneously is low - thus the 75% reductions are allowed.
This makes sense for a buildng where people WOULD occupy the building during a windstorm. However, this tower is outdoors and it seems that the chance of a full live load with full wind would be EVEN LOWER. Would you ever get even close to 100% LL with a heavy wind blowing? I don't think so. But it appears that I'm locked into the 75% reduction.
Does it make sense to lower that combination to this:
D + 0.5L + 0.75W
D + .75L + 0.5W
There's no code justification for it - just common sense?