If you are refering to 680.26.B.3, 4 inches is the largest dimension permitted for an isolated metal part within the swimming pool that is not required to be bonded. It is not a clearance requirement. For swimming pool installations, I strongly recommend consulting with a licensed electrical engineer experienced with swimming pools.
I assume it's because they feel like it is unlikely for something that small to accidentally become energized or that someone may be in contact with it.
"All metal fittings within or attached to the pool structure shall be bonded. Isolated parts that are not over 100 mm ( 4in.) in any dimension and do not penetrate into the poll structure more than 25 mm (1 in.) hall not require bonding."
Does that mean that if an isolated part is over 4", but does not penetrate the pool structure by more than 1", it also does not require bonding?
rjohnston
I read your other post in the corrosion forum.
What are the large structures for, or can't you say?
The corrosion guys seemed to have got a handle on the corrosion potential.
Is it a swimming pool or do we evacuate the fish because of zinc poisoning?