Please refer to the attached sketches.
My client has requested that I evaluate his existing building for its ability to support an additional story. Upon review of the drawings, I discovered a couple of foundation detailing errors that I believe to be quite serious. So serious, in fact, that I doubt that the foundation could be shown to have enough capacity to support the number of stories that the building currently has.
The detailing errors that I'm concerned with both involve "property line" footings along one side of the building. Specifically:
1) Some of the load delivered to the foundation system along the property line is delivered as concentrated loads (columns). The original designer placed eccentric pad footings beneath those concentrated loads and balanced things by providing strap beams back to interior columns. The trouble is that, according to my understanding of things, the strap beams have been reinforced bass-ackwards. They've been provided with bottom steel but no top steel. In my mind, this error renders them pretty much useless.
2) Some of the load delivered to the foundation system along the property line is delivered as uniform loads. Unfortunately, as detailed, I have little confidence in the ability of the footing / wall connection to transfer moment. To me, it looks like just a regular wall plopped down on a regular footing. It'll have some moment capacity, no doubt, but I feel that it will be unreliable and difficult to assess.
So my questions are these:
1) Do others agree with my assessment of things here? Might there be something that I've overlooked that would improve matters?
2) Does anyone have any clever ideas for a repair? I've got exactly one so far and I'm not terribly enamoured with it. See the bottom detail in the attached sketch.
Thanks for your help.
KootK
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.
My client has requested that I evaluate his existing building for its ability to support an additional story. Upon review of the drawings, I discovered a couple of foundation detailing errors that I believe to be quite serious. So serious, in fact, that I doubt that the foundation could be shown to have enough capacity to support the number of stories that the building currently has.
The detailing errors that I'm concerned with both involve "property line" footings along one side of the building. Specifically:
1) Some of the load delivered to the foundation system along the property line is delivered as concentrated loads (columns). The original designer placed eccentric pad footings beneath those concentrated loads and balanced things by providing strap beams back to interior columns. The trouble is that, according to my understanding of things, the strap beams have been reinforced bass-ackwards. They've been provided with bottom steel but no top steel. In my mind, this error renders them pretty much useless.
2) Some of the load delivered to the foundation system along the property line is delivered as uniform loads. Unfortunately, as detailed, I have little confidence in the ability of the footing / wall connection to transfer moment. To me, it looks like just a regular wall plopped down on a regular footing. It'll have some moment capacity, no doubt, but I feel that it will be unreliable and difficult to assess.
So my questions are these:
1) Do others agree with my assessment of things here? Might there be something that I've overlooked that would improve matters?
2) Does anyone have any clever ideas for a repair? I've got exactly one so far and I'm not terribly enamoured with it. See the bottom detail in the attached sketch.
Thanks for your help.
KootK
The greatest trick that bond stress ever pulled was convincing the world it didn't exist.