@rapt:
As far as the raw facts go, I agree with all of your last post. It is consistent with, and is a natural extension of, the derivation that I presented above (details A/B/C). What I still disagree with, somewhat, is the perspective taken. Everything that follows will be stated with unbonded PT in mind, to the extent that does or doesn't matter.
rapt said:
The concept of "balanced load" is simply a method of visualizing and calculating the effects of the change in tendon curvature...and this is exactly equal to P.e. They are simply 2 methods of calculating the same thing.
To me, this implies that Pxe is the real physical phenomenon and balanced load effects are a convenient construct for "visualizing and calculating the effects of the change in tendon curvature". I believe that it's the other way round: the balanced load effect is really and truly applying transverse load to the member, in service and at ultimate, and it is Pxe that is the convenient construct for visualization and calculation.
At the ends of a member, the center of compression starts off at the anchorages. The physical action that shifts the center of compression to coincide with the tendons as we move along the length of a member is the balancing load effect. That's what
gets it done as it were.
At the start of this thread, I was trying to double dip with regard to the balancing load. And that was wrongheaded. However, I still find statements to the effect of "balancing loads have nothing to do with ultimate flexural capacity" to be rather misleading. I believe that what people really mean, or should mean, when they make such statements, is:
1) Our standard calculation procedure does not explicitly include balancing load effects and/or;
2) Balancing load effects should be included once in the formulation, not twice.
Were it not for the balancing load effects, when we calculated ultimate flexural capacity of a member, the post-tensioning force would have to be located at the elevation of the anchorages rather than at the elevation of the tendon. Viewed in that sense, the balancing load effects have a significant impact on ultimate flexural capacity.