I would appreciate all your opinions on this as a sanity check. I have been asked to look at an existing pre-engineered metal building for snow drift from a new higher length extension. There is no question that I will need to review the purlins and eave struts to the current code for this new snow drift. The frames are a different story and I will explain.
The only two frames affected by the length addition snow drift are the endwall frame and the next frame in. The same frame was used in both locations and the original reactions indicate that both frames were designed for a 25' trib and 30 psf roof snow load. The new length extension is self supporting so the endwall frame only has a trib of 13.125'. The current code only requires a balanced roof snow load of 20 psf. When all is said and done both frames are carrying less total snow load when I use the minimum 20 psf snow load in combination with the snow drift than the original 30 psf.
Can I make the argument that since the new code required snow loading does not exceed the original designed snow loading that no review of the frames is required and they do not need to be brought up to the current code
Thanks!
The only two frames affected by the length addition snow drift are the endwall frame and the next frame in. The same frame was used in both locations and the original reactions indicate that both frames were designed for a 25' trib and 30 psf roof snow load. The new length extension is self supporting so the endwall frame only has a trib of 13.125'. The current code only requires a balanced roof snow load of 20 psf. When all is said and done both frames are carrying less total snow load when I use the minimum 20 psf snow load in combination with the snow drift than the original 30 psf.
Can I make the argument that since the new code required snow loading does not exceed the original designed snow loading that no review of the frames is required and they do not need to be brought up to the current code
Thanks!