Engineer6512
Mechanical
- Nov 4, 2002
- 67
I am in the process of sizing a new pump to increase the flow rate in my system from about 850 gpm to 970 gpm. The system has an existing control valve, and I simply want to determine whether the existing valve will be acceptable at the new flow rate, or if I have to install a new one.
My thinking is that I will calculate the Cv at the new flow rate and use the manufacturer's chart to see how much the valve is open at the new flow rate. As long as it's still in the 50 - 80% range the existing valve should be ok. If it's outside this range, I should probably size and install a new valve.
So, I know my new flow rate, I have the valve Cv chart, the only unknwn left in the equation is what to use for the delta-P across the valve? The usual way of sizing a control valve is to take Pump discharge pressure and subtract losses and final required system pressure. The problem is that I need to know the delta-P of the Control Valve to calculate the discharge pressure required for my pumps! So do I just assume a delta-P for the CV (I read somewhere that 30% of Total system pressure drop is common), and go from there? Or am I missing something?
Some guidance here would be greatly appreciated.
Thanks.
My thinking is that I will calculate the Cv at the new flow rate and use the manufacturer's chart to see how much the valve is open at the new flow rate. As long as it's still in the 50 - 80% range the existing valve should be ok. If it's outside this range, I should probably size and install a new valve.
So, I know my new flow rate, I have the valve Cv chart, the only unknwn left in the equation is what to use for the delta-P across the valve? The usual way of sizing a control valve is to take Pump discharge pressure and subtract losses and final required system pressure. The problem is that I need to know the delta-P of the Control Valve to calculate the discharge pressure required for my pumps! So do I just assume a delta-P for the CV (I read somewhere that 30% of Total system pressure drop is common), and go from there? Or am I missing something?
Some guidance here would be greatly appreciated.