Same words, different meaning.
The 15 seconds is not shown in the wave form recording.
It may be a 15 second delay
before the fast transfer.
It is common to have a 15 second delay before retransfer. If, for instance, a line is closed into a shorted distribution transformer, the re-closers may re-close several times in 15 seconds. Each re-close will reset the 15 second timer. The 15 second delay ensures that the re-closers are not operating. Then there is a fast transfer. This is one mode of operation.
Just because something is set to 15 seconds does not mean that there is a 15 second open circuit delay between source A and source B.
OP said:
Further, if phases on alternate source B are not correctly connected to ATS (for example, mixed A/B/C) would this be a potential issue?
Yes. That's what I have been trying to explain. Should be A-A, B-B, C-C.
A-B, B-C, C-A will give the same rotation but may cause issues on a fast transfer,
No the motors won't be running backwards.
WAG: The back EMF is quite close to the applied voltage. The discontinuity happens on a falling wave form. If the back EMF is lagging, the
instantaneous back EMF may be greater then the applied voltage. Just a guess for discussion.
It looks like an event every 3 cycles. I don't understand that.
Transformer inrush can happen with a step voltage increase at the wrong point on wave. The inrush may be 25 times FLA.
This may be an issue with the battery charger transformers and improper phasing of the sources.
PLEASE VERIFY THAT BOTH SOURCES ARE A-A, B-B, and C-C.
Keith and others: Feel free to speculate.
Can you provide the make and model of the ATS. That will eliminate a lot of speculation.
Bill
--------------------