I've seen an excess flow valve sometimes used in combination with a rupture disk/PSV. Unfortunately, I lack the ability to send a sketch that would make the arrangement clear. Instead let me try to describe the configuration.
1) Starting at the vessel being protected,
2) Fluid flows to rupture disk, then
3) Through a tee fitting.
4) In the branch of the tee, locate the excess flow valve.
5) One side of the excess flow valve is connected to the tee.
6) The other side of the excess flow valve is open to atmosphere or other suitable destination.
7) Install the excess flow valve so that high flowrates from the tee to atmosphere will cause the valve to close.
8) Install a pressure gauge upstream or downstream of the tee.
9) Install the PSV downstream of the pressure gauge connection.
The idea is that the rupture disk could develop a leak. You want to know about the leak so you can replace the rupture disk. Presumably, it is undesirable to have the PSV pop, else why even bother with the rupture disk. Thus if the rupture disk actually pops due to overpressure, the excess flow valve will close and the full pressure will be experienced at the PSV inlet. The pressure gauge will indicate this high pressure, so it will be apparent that the rupture disk has burst.
Instead, if the rupture disk just develops a small leak, it will escape through the excess flow valve.
That's what I've seen. As I think about it, I believe the situations where you would want this type of performance are quite limited.
Doug