The critical loads are on the auxiliary AC/DC system to operate the substation safely in the event of loss of power ehither locally or remote. Keep in mind that substations is an inportant facility that should have high degree of availability during and after the ocuurence of disaster.
Typicall critical loads are as follow:
1- DC subsystem (Baterry charger, UPS)
2- Communication for protection & voice(SCADA, PLC, radio,etc)
3- Control circuit (lights, relays, microprocessor equipment, mimic panels, etc)
4- Monitoring and supervisoring equipment(printer,GPS, Fault & event recorder,computer & monitor, etc.)
5- Local annuciator and Alarm system.
6- External & Internal lighting.
7- Security system (Intrussion, CCVT, etc)
8- Fire alarm circuits
9- Maintenance receptacle.
10-Other vital equipment if require(HVAC, pump,Motor operate equipment, compressor,etc.)