alannakate
Structural
- May 18, 2011
- 12
Hello,
I'm struggling to figure out the simplified method vs the equivalent static method in the seismic portion of the 2015 National Building Code of Canada.
The seismic hazard index is listed as IeFsSa(0.2) and IeFsSa(2.0) (Cl. 4.1.8.1 (2)). If these values are less than 0.13 and 0.03 then building is in the low seismic zone and the simplified method can be used.
Conversely, if IeFaSa(0.2) (NOT IeFsSa(0.2)) is less than 0.35, the equivalent static method can be used. I ran through a basic example (a 3 storey, braced steel frame, normal importance) using both methods and found the simplified method to give a significantly more conservative shear force than the equivalent static method. (The CISC does a similar example here:
My question is, why has the simplified method been added? If your building fits in the low seismic category then in many cases (at least where I live in Halifax) it also qualifies for the equivalent static method. Why would I choose to go with the simplified method over the equivalent static method if both are applicable and one leads to a significantly more conservative lateral bracing design and thus more steel, ect?
Thanks for any insight on this.
I'm struggling to figure out the simplified method vs the equivalent static method in the seismic portion of the 2015 National Building Code of Canada.
The seismic hazard index is listed as IeFsSa(0.2) and IeFsSa(2.0) (Cl. 4.1.8.1 (2)). If these values are less than 0.13 and 0.03 then building is in the low seismic zone and the simplified method can be used.
Conversely, if IeFaSa(0.2) (NOT IeFsSa(0.2)) is less than 0.35, the equivalent static method can be used. I ran through a basic example (a 3 storey, braced steel frame, normal importance) using both methods and found the simplified method to give a significantly more conservative shear force than the equivalent static method. (The CISC does a similar example here:
My question is, why has the simplified method been added? If your building fits in the low seismic category then in many cases (at least where I live in Halifax) it also qualifies for the equivalent static method. Why would I choose to go with the simplified method over the equivalent static method if both are applicable and one leads to a significantly more conservative lateral bracing design and thus more steel, ect?
Thanks for any insight on this.