I'm working on a project where I received structural calculations for a piece of equipment which is around 10'x12'x35' tall and weighs approximately 100K. We are responsible for the base plate design (a bit unusual), anchorage and foundation. After reviewing the calculations, I discovered that the design included a total of 3 load combinations. While they were called Dead Load, Wind Load, and Seismic Load, I discovered that they were really DL, DL + W, and DL + EQ. Their single wind load was a wind load in the X-Z plane (y being vertical)... essentially acting on the diagonal.
They reported that the moment due to wind was around 300K-ft (on the equipment drawings and in their calculations). After digging a bit, I found that the moment due to wind was actually around 700K-ft but they subtracted the resisting moment (~100K*10'... the dead load times the distance from the centroid to the furthest anchor point) from the wind moment. Yes, they took Mwind-Mres as their wind moment even though the resisting moment was larger than their wind moment.
I discussed over the phone with him my questions and he got rather defensive. I asked whether he included the 0.7 factor on his seismic loads to move it from an ultimate load to a service level load to which he replied 'I'm not sure what you mean by ultimate load.' His PE status indicates that he is a mechanical engineer.
My biggest request was to include wind loads in the X and the Z plane as I believe this is normal practice and can produce more realistic/governing designs for all of the base plates and anchorage. His response was that he believes that this is an additional service and will charge our client to perform this task.
Any suggestions on how to proceed? As a structural engineer, I believe there is enough conservatism in some of the loading and can back out some information that is required, however i will be forced to make a lot of assumptions in order to get what i feel is a comprehensive design completed.
They reported that the moment due to wind was around 300K-ft (on the equipment drawings and in their calculations). After digging a bit, I found that the moment due to wind was actually around 700K-ft but they subtracted the resisting moment (~100K*10'... the dead load times the distance from the centroid to the furthest anchor point) from the wind moment. Yes, they took Mwind-Mres as their wind moment even though the resisting moment was larger than their wind moment.
I discussed over the phone with him my questions and he got rather defensive. I asked whether he included the 0.7 factor on his seismic loads to move it from an ultimate load to a service level load to which he replied 'I'm not sure what you mean by ultimate load.' His PE status indicates that he is a mechanical engineer.
My biggest request was to include wind loads in the X and the Z plane as I believe this is normal practice and can produce more realistic/governing designs for all of the base plates and anchorage. His response was that he believes that this is an additional service and will charge our client to perform this task.
Any suggestions on how to proceed? As a structural engineer, I believe there is enough conservatism in some of the loading and can back out some information that is required, however i will be forced to make a lot of assumptions in order to get what i feel is a comprehensive design completed.