Sorry I need to supplement that this is a reinforced concreted structure
Dear JLNJ,
The structure in my model is mainly resisted by shear wall under wind load. Therefore this column has little contribution in lateral stability. It mainly support the gravity load of cantilever portion at this structure. If I model it as rigid joint, the whole part act as somehow like portal frame in vertical direction to support the cantilever portion load. If I model it as pin support, the cantilever load mainly act on the three beam directly. However, the column size is restrained in my case while beam size is capable of taking the moment even column is pinned
Dear KootK,
I plan to design the beam column connection as rc moment connection with sufficient anchorage as In reality, the column will experience certain degree of bending. However, I make sure that the transfer beam is well designed such that it provide sufficient bending capacity by assuming column is pinned in the model. Is there any concern for my assumption.
My major concern is, the beam column connection is moment joint for rc detailing, the column is continuous all along the two floors. Even though, can I assume it as a pin joint? My thought is, I indeed conservatively treated this joint, and conservatively designed the beam under this assumption. Like people commonly model column base detailing into foundation as pin joint, indeed they use full anchorage reinforcement in detailing
Thanks all for addressing my concern