I understand the conditions for a partially enclosed building per ASCE 7. It states:
1. the total area of openings in a wall that receives positive external pressure exceeds the sum of the areas of openings in the balance of the building envelope (walls and roof) by more than 10%, and
2. the total area of openings in a wall that receives positive external pressure exceeds 4 ft2 (0.37 m2) or 1% of the area of that wall, whichever is smaller, and the percentage of openings in the balance of the building envelope does not exceed 20%.
Both conditions must be met.
However, I have a questions about buildings in a hurricane prone region. Per the ASCE Guide to the use of wind load provisions, it states that if the windows are not wind-borne debris rated, then you should be designing as a partially enclosed building.
My question is: why doesn't condition #1 need to be met? I have a hard time getting the numbers to work out to meet condition #1. For example, lets use a square office building with the same window pattern on all four sides. If we say that all the windows fail, how do the total openings on the positive face exceed the sum of the other three sides by 10%?
I would love to hear your input!
Thanks in advance.
Brian
1. the total area of openings in a wall that receives positive external pressure exceeds the sum of the areas of openings in the balance of the building envelope (walls and roof) by more than 10%, and
2. the total area of openings in a wall that receives positive external pressure exceeds 4 ft2 (0.37 m2) or 1% of the area of that wall, whichever is smaller, and the percentage of openings in the balance of the building envelope does not exceed 20%.
Both conditions must be met.
However, I have a questions about buildings in a hurricane prone region. Per the ASCE Guide to the use of wind load provisions, it states that if the windows are not wind-borne debris rated, then you should be designing as a partially enclosed building.
My question is: why doesn't condition #1 need to be met? I have a hard time getting the numbers to work out to meet condition #1. For example, lets use a square office building with the same window pattern on all four sides. If we say that all the windows fail, how do the total openings on the positive face exceed the sum of the other three sides by 10%?
I would love to hear your input!
Thanks in advance.
Brian