I need some help with something. We are having trouble starting 3 ea. 60 hp booster pumps with PFC (Capacitors) and then starting a 300 hp well pump with solid state starter.
The generator is an 800 kW.
It is tripping out for under frequency when we start the well pump after the booster pumps, but it is not actually dropping under load.
If we remove the capacitors from the booster pumps, everything works fine.
If we start the well pump first, then start the booster pumps, everything is fine.
There appears to be a problem with the capacitors and solid state starter.
The engineer has to start the booster pumps first, and then the well pump.
He also has to keep the capacitors on the booster pumps to help with the utility side, something to do with useage.
It is a Newage Alternator.
Have you got any suggestions on how we can make this work in the sequence they require?
Thanks for any help.