EMBEDMENT OF PILE INTO THE PILE CAP

Status
Not open for further replies.

engineeringofcivil

Civil/Environmental
Joined
Jun 20, 2006
Messages
8
Location
IN
It is conventional to embed the concrete pile in the pile cap by 3/4 inch . Is this a good practice to give an idea firming of pile upto the cap. Do we get any advantage in lateral/uplift load sharing.
Can some one tell me whether it is mandatory as per any code
 
EngofC - Whats an "idea firming"?

Our structural embed the pile 75mm into the pile cap I understand. I dont think 3/4 inch is sufficient, just by judgement...
 
sorry typo. I like to mean proper formation of pile upto cut off level
 
2018 IBC section 1810.3.11 requires 3" embedment
 
For your information, posting in more than one place here is frowned upon. We all look at many rooms.
 
3/4" would give you a small bit of additional shear capacity at the interface, but we usually use 3" to give us the greatest increase in shear capacity without affecting the reinforcing in the bottom of the cap, which is 3" clear.
 
I've always used 75mm (i.e. about 2.5")
 