DTS419
Structural
- Jun 21, 2006
- 180
In ACI 318-14 17.5.2 Concrete breakout strength of an anchor in shear, the only time the embedment depth of the anchor (h-sub-e) comes up is in Fig. 17.5.2.1a. However, in this figure it is not clear how the embedment depth relates to the depth of the failure zone, shown as 1.5 * ca1 (edge distance).
In Fig. R17.5.2.1b, the critical depth is defined either by the member thickness (h-sub-a), or 1.5 * ca1 and embedment depth is not a factor in either.
Let's say you had a relatively large edge distance, but a very shallow anchor embedment depth. You would calculate the same breakout strength based on the edge distance whether the anchor is embedded 8" or just 1/2" which doesn't seem right, so I must be missing something.
How does embedment depth relate to the depth of the failure zone and breakout strength of the anchor?
In Fig. R17.5.2.1b, the critical depth is defined either by the member thickness (h-sub-a), or 1.5 * ca1 and embedment depth is not a factor in either.
Let's say you had a relatively large edge distance, but a very shallow anchor embedment depth. You would calculate the same breakout strength based on the edge distance whether the anchor is embedded 8" or just 1/2" which doesn't seem right, so I must be missing something.
How does embedment depth relate to the depth of the failure zone and breakout strength of the anchor?