Dear Mr. Mbrooke
Q. ... What is the highest molded case or PC breaker size a manufacturer sells without electronics? Just bi-metal and coil elements. I'm reading 225 amps..."
A1. "Just bi-metal and coil elements " is termed "thermalmagnetic" by some manufacturer. The "thermal" is by (bi-metal) for [over-load], while the "magnetic" is by (electromagnet) for [short-circuit] protection. They are suitable for ac or dc networks. Numerous MCCB manufacturers with "thermalmagnetic" release up to 630A; in the IEC world. As for PC breaker = ACB (per IEC), "electronic" release prevail.
A2. For MCCB, the "thermal" is usually adjustable from say 0.6... 1.0In. While the " magnetic" may be fixed at 3,5,10In etc or adjustable 5-10, 6-14In etc., where In=rated current (of the breaker). e.g. breaker In=630A, the "thermal" may be adjustable from say 0.6 ....to 1.0In. The "magnetic" fixed at 5 or 10In or adjustable from 5...10In.
A3. For ACB:
a) electronic release may encounter problem to operate at very low say 1 to 5%In, e.g. for earth fault protection, as the voltage generated by the internal CT may not be sufficient to operate the electronic release. This can be circumvented by having external dc auxiliary supply to ensure that the voltage is sufficient to operate correctly.
b) there is no serious problem reported " due to radiated EM energy in a long time ". This is evident that electronic release prevail on the market.
Che Kuan Yau (Singapore)