Hi,
A casual worker was superficially burned on the fingers when a power cable was accidently put into contact with the frame. The worker was touching the frame at this particularly instant. The 63 Amps MCB did trip but was not fast enough to prevent the accident.
According to the IEC rules, RCDs are not to be used on TN-C systems.RCDs should ONLY be used in the TN-S part of the system, meaning after splitting the PEN-condutctor into one PE- and one N-conductor. As a summary, RCDs should not be used in systems with PE- and N-conductors combined (as for the TN-C).
According to me, the RCD can be omitted in TN-systems as long as you can prove that the MCB will disconnect within a certain amount of time According to IEC60364, for TN-systems and protection against electrical shock:
413.1.3.3: It is said that Zs*Ia <= U0, i.e. system-impedance multiplied by the minimum current that assures that the breaker is disconnected within a given time should be less than the nominal phase-voltage.
The time is given as a table, and for U0=230V (i.e. TN Ull=400V) the maximum time is 0,4 seconds.
If the minimum fault current that occurs is quite large, and the system-impedance is kept quite low, you should be able to fulfill this requirement with a MCB, depending on it's caracteristics.
Bob
A casual worker was superficially burned on the fingers when a power cable was accidently put into contact with the frame. The worker was touching the frame at this particularly instant. The 63 Amps MCB did trip but was not fast enough to prevent the accident.
According to the IEC rules, RCDs are not to be used on TN-C systems.RCDs should ONLY be used in the TN-S part of the system, meaning after splitting the PEN-condutctor into one PE- and one N-conductor. As a summary, RCDs should not be used in systems with PE- and N-conductors combined (as for the TN-C).
According to me, the RCD can be omitted in TN-systems as long as you can prove that the MCB will disconnect within a certain amount of time According to IEC60364, for TN-systems and protection against electrical shock:
413.1.3.3: It is said that Zs*Ia <= U0, i.e. system-impedance multiplied by the minimum current that assures that the breaker is disconnected within a given time should be less than the nominal phase-voltage.
The time is given as a table, and for U0=230V (i.e. TN Ull=400V) the maximum time is 0,4 seconds.
If the minimum fault current that occurs is quite large, and the system-impedance is kept quite low, you should be able to fulfill this requirement with a MCB, depending on it's caracteristics.
Bob